Hi, In the lobby, I have the following:
I would expect to see the M Flow at extract fan = M Flow at doors+ M flow from leakage, but there is a slight error (10%). When simplifying the model, I believe this is caused by the localised leakage (if there is no leakage, M Flow at extract fan and the M Flow at doors perfectly matches up). Can you confirm if this is likely to be the case, and if so is there any way to get an accurate value for the mass flow rate across the localised leakage? |
Beta Was this translation helpful? Give feedback.
Replies: 2 comments 1 reply
-
Leakage is implemented as an HVAC vent. There is a table in the User's Guide listing output for HVAC networks. |
Beta Was this translation helpful? Give feedback.
-
Beta Was this translation helpful? Give feedback.
Based on your post it sounds like you want to measure mass flux at the wall (purple arrow) but are using a gas phase measurment (orange). When measuring away from the wall, you have the possiblity for air from cells around the leakage vent to be entrained into the leakage flow (green arrows). As Kevin noted you can output the actual mass flow in the virtual duct being used for each leakage path.