Are your colleagues / the AHJ correctly interpretting the intent of BR 386? The only meaningful constant value for a radiant fraction would be from the flame volume. A global fraction including all impacts from the plume / hot surfaces / etc. cannot be a prescribed constant as the details of confinement and relative fire size would start to matter. |
Beta Was this translation helpful? Give feedback.
-
I have not talked with the AHJ, so my knowledge on their understanding is second hand. The requirement comes from the statement below. This looks to be in line with specifying a global Q_RADI/HRR. My thought is that the BR 386 guidance is tailored more to empirical and zone model calculations since it was published in 1999 before CFD fire modeling was widely used. "Table 3.3 summarizes several of the more commonly adopted steady-state design fire sizes in current use. The heat release rate (qfAf) is the total heat generated by combustion per second, and is the parameter measured in most calorimetry experiments. Some of this heat is |
Beta Was this translation helpful? Give feedback.
-
Maybe we should clarify that BR 368 is a 1999 document, "Design methodologies for smoke and heat exhaust ventilation", published by CRC Ltd with the permission of the UK's Building Research Establishment. As far as I can tell, that document does not actually specify a radiative fraction -- is that correct? What it does is specify values of "Total convective heat flux" for some official or semi-official design fire sizes, which are clearly larger. The difference between the total fire size and the convective fire size is not discussed, but it is presumably a radiative fraction in some sense. This approach is clearly not thinking about fire chemistry or even plume size in any detail at all -- so the convective heat flux for a sprinklered hotel room could be 400kW "close to the plume" or 300kW "at the window", out of a total of 500kW (deduced from fire area 2 m^2 and heat release rate density 250 kW/m^2). I don't know where the missing 100kW or 200kW is supposed to have gone. I agree with the idea that BR368 quoted these values for use in zonal models and not in CFD. The design fire sizes were copied in British Standard BS7346-4 in 2003 (and still valid), but the column of convective fire sizes was omitted. I have always hoped that the RADIATIVE_FRACTION parameter in FDS is not critical for my simulations, which almost always involve large fires and appreciable soot fractions. The path length for radiation anywhere near the fire is much less than 1m, so I have assumed that convection and radiation would reach equilibrium with each other within a few metres (and probably a lot sooner). The RADIATIVE_FRACTION parameter is effectively a starting guess in this equilibrium. If a different value was specified, I would expect to see a somewhat different flame temperature, and hence probably a slightly different plume size, but the same amount of heat has to leave the fire bed, and it will leave in more or less the same way. Is this a fair summary? (I know, I should check the sensitivity in my models -- but it's not at the top of the list of sensitivities to investigate.) |
Beta Was this translation helpful? Give feedback.
-
I don't follow the reasoning as to how the |
Beta Was this translation helpful? Give feedback.
-
The whole concept of radiant fraction as commonly used in fire protection is based on measurements made of fires in the open. That 35 % radiant fraction does not apply as a global value once you start confining the fire and the fire plume. I don't think it is appropriate in a design application to set QR_CLIP = -1 so the RADIATIVE_FRACTION is treated as global as there is no way you would know the global fraction for a specific geometry a priori. In reality, when you add more and more hallway length, the fire is going to radiate the same nominal amount as when it was in the open and as you increase the hallway length and have more and more length of upper layer the loss from the upper layer will increase. Overall the global value increases but the fire is going to stay more or less the same. Setting QR_CLIP = -1 has two large issues. 1) To get the correct radiant source term as the real fire you would need to up the RADIATIVE_FRACTION but you don't know by how much. 2) The reason we need correction is we don't resolve the 2000 K flamelet temperature on an egineering grid. At most we get up to 1000-1200 K. In the layer down the hallway. however, that temperature is a good temperature for the source term from that gas. There is no unresolved flame down the hall. Correcting the flame volume and the hall layer with the same factor would not be physically valid. |
Beta Was this translation helpful? Give feedback.
-
Now I understand where Jonathan is coming from. The |
Beta Was this translation helpful? Give feedback.
-
I think there should be a distinction between your developer-level discussion (which I do not completely follow) and what users should be adjusting (which is how the original question was posed). For modelling smoke in hallways, I do not think it is necessary or appropriate to adjust C_MIN, C_MAX or QR_CLIP. I do not see any requirement to match some convective/radiative info in the BR 368 document -- whatever results come out of the FDS model are likely to be more realistic than a pre-specified fraction. None of the validation cases alter those three parameters, except the McCaffrey plume set, which concerns radiation measurements from soot-free flames. I'm approaching this from the perspective of models where the flames are optically thick, and heat loss to walls near the flame is not a critical result -- in that context, I don't see any need at all to tinker with those settings. Please correct me if I'm wrong on this. |
Beta Was this translation helpful? Give feedback.
-
Some of my colleagues were discussing how they handle RADIATIVE_FRACTION in PBD in their regions. The issue they run into is that the local authorities want designers to follow BR 368 which species a radiative fraction as part of the recommendations. When they run a case with the default FDS parameters, the global radiative fraction does not match the user prescribed.
I looked into their case in a bit more detail and wanted to start a discussion here. The attached cases compare a slightly modified version of the Verification/Pressure_Solver/hallways.fds case. The modifications were to expand the range on QR_CLIP, C_MIN, and C_MAX such that the global radiative fraction should match the user specified and compare these with the FDS defaults. Initially, the global radiative fraction for all 3 cases matches the specified value for propane at 0.29. The cases start to diverge much more quickly than I was expecting before running the simulations.
This is not a bug since FDS is doing what the design documentation says it is doing. The question I have is whether the design meets the intended objective of matching the global radiative fraction. It seems unintuitive to me to have C_MIN < 1 if the goal of RADIATIVE_FRACTION is to account for unresolved flames. Thoughts?
hallways.zip
Beta Was this translation helpful? Give feedback.